Originally posted by John Osvatic:
I was told that if you measure the circumference of a solid number six ground wire and then do the same with each individual strand of a stranded number six you will get a larger over all circumference plus in addition to the flexability of stranded.
PS: I did have a situation where my crew had to change out numerious solid ground wires to stranded per the inspector.
If any of that were true the current carrying capacity of the cable or wire would be increased for stranded. Also, how would you explain a six strand vs a 18 vs a 30? Fact is the cross section is made to be the same regardless of whether the wire is solid or stranded. Plenty of ignorant sparkies out there though and that's probably where your story came from. And the inspector was an idiot for the same reason.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Dec 2005
Posts: 7,056
RIP Moderator-Mitel, Panasonic
*****
Offline
RIP Moderator-Mitel, Panasonic
*****
Joined: Dec 2005
Posts: 7,056
There is 1 valid reason for using stranded rather than solid 6ga. IT'S A LOT EASIER TO PLACE! You don't need a mallet to make stranded conform to the variations in surface flatness!


When I was young, I was Liberal. As I aged and wised up, I became Conservative. Now that I'm old, I have settled on Curmudgeon.
Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
Quote
If any of that were true the current carrying capacity of the cable or wire would be increased for stranded. Also, how would you explain a six strand vs a 18 vs a 30? Fact is the cross section is made to be the same regardless of whether the wire is solid or stranded. Plenty of ignorant sparkies out there though and that's probably where your story came from. And the inspector was an idiot for the same reason.

-Hal
Hal, I'm wondering if the inspector was basing his demand upon the fact that the NEC requires anything larger than #8 to be stranded for building wiring.

Frankly, I base all of my practices in the telecommunications business on Bell System Standards. All they ever used for premise grounding conductors was solid copper. With the exception of FiOS installations, Verizon appears to be holding true to the BSP for everything else.


Ed Vaughn, MBSWWYPBX
Joined: Feb 2005
Posts: 12,344
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,344
Likes: 3
Hal, I'm wondering if the inspector was basing his demand upon the fact that the NEC requires anything larger than #8 to be stranded for building wiring.

Maybe. We do have #6 solid, bare or with a telephone gray PVC jacket and they don't.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Joined: Mar 2002
Posts: 3,630
Z-man Offline OP
Moderator-Avaya, Nortel
OP Offline
Moderator-Avaya, Nortel
Joined: Mar 2002
Posts: 3,630
I think their request for braided was based solely on two things... Looks and Looks.. these guys care more about it looking pretty than it working right. It is one of those dog and pony locations. The braided wire was just the start..don't get me going on their patch cord requirements.....


Z-man
Avaya SME Authorized Partner
www.omniofficetech.com
Page 3 of 3 1 2 3

Moderated by  Silversam 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,291
Posts638,815
Members49,767
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,399 Shoretel
189,145 CTX100 install
187,423 1a2 system
Newest Members
Robbks, A2A Networks, James D., Nadisale, andreww
49,767 Registered Users
Top Posters(30 Days)
Toner 26
teleco 6
dexman 5
jsaad 4
Who's Online Now
0 members (), 149 guests, and 429 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5