Yes, the twin cable that you reference is quite common for circuit extensions. In order to work properly, the transmit pair for the circuit should reside in one shielded jacket and the receive pair should be in the other. These are usually four pair cables, meaning that four circuits can be extended in the single cable run.

In a perfect world, four transmit pairs reside in one cable and four receives are in the other one.

The cable shields should be bonded together and tied to the building's grounding electrode conductor, although any local ground connection at the service entrance will usually suffice. These cables should NEVER be bonded at both ends.

As for the jack pins with regard to grounding: Don't even think about that part. As long as the cable shielding is properly bonded to the building's electrical ground, this additional bonding isn't really necessary.

T1 circuits often arrive to the premises via thousands of feet of "CAT 0" copper cable, but once they hit the smart card, NIC, NTU, NTC or whatever they call them these days, the circuit must be treated a bit more gingerly.

You are correct in your assumption that a traditional CAT (anything) cable tester won't confirm proper operation of a T1 circuit extension. This is due to the fact that a T1 circuit isn't a LAN circuit; it is a network connection. These are completely separate aspects of the telecom industry.

I must commend you for even asking these questions. Circuit extensions are quite often misunderstood since they take on a whole new life once they hit that network termination card.


Ed Vaughn, MBSWWYPBX
Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Aug 2009
Posts: 278
Member
Offline
Member
Joined: Aug 2009
Posts: 278
Okay the shields for each pair and for each cable sheath should all be grounded at the service entrance. I can probably get away with putting a screw into the shelf or cabinet right next to where I put my plug into the smart jack. I have seen that these cabinets are usually bonded to a good ground.

What is the best way to connect these foil or braided sheilds together so I can screw them down to the metal cabinet? What part would I actually use to make this connection? In other words, in actual physical terms, how do I bond these delicate aluminum or braided shields to the ground?


Vaya con Dios amigos!
Butch
Joined: Aug 2009
Posts: 278
Member
Offline
Member
Joined: Aug 2009
Posts: 278
Bump -- Any ideas here?


Vaya con Dios amigos!
Butch
Joined: Dec 2002
Posts: 9,424
Likes: 1
Member
*****
Offline
Member
*****
Joined: Dec 2002
Posts: 9,424
Likes: 1
The other day I saw an install where they used 2 pair shielded wire. The drain wires were all under a lug on the smartjack, and then just punched down on the block. I guess that defeats the purpose of a shield!


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
Joined: Aug 2009
Posts: 278
Member
Offline
Member
Joined: Aug 2009
Posts: 278
Ed said to ground the shields at the service entrance only, not at the extended demark. So what you just describes sounds like it should work. I guess you can just gather up all the drain wires (shielding) and twist them together and screw them down to the smart jack cabinet.

I think maybe if you have a small grounding clamp or small metal hose clamp, you can bend all the shield wires and foil back over the outside of the cable sheath and then clamp a grounding/bonding wire down to them.

I would sure like to know the official/profesional-looking/NEC way of doing this. Maybe that is it?

If any of you were around in the old days when network cabling was all done with shielded twisted pairs, you can enlighten us on how the shield bonding is done.

I have another idea. Instead of buying special twinned double-shielded T1 cable, can we use a couple of old shielded twisted pair cables? There is tons of this stuff laying around in phone rooms.


Vaya con Dios amigos!
Butch
Joined: Oct 2010
Posts: 250
Member
Offline
Member
Joined: Oct 2010
Posts: 250
"and twist them together and screw them down to the smart jack cabinet".

"and screw them down under the ground lug on the smart jack cabinet IF the installer grounded the smart jack cabinet properly".


Forty six years and still fascinated with Telecommunications!
Joined: Oct 2010
Posts: 250
Member
Offline
Member
Joined: Oct 2010
Posts: 250
There is no NEC on T1 demarc extensions. What is regulated is what test parameters must be passed before telco can turn the T1 over to the customer. QRSS, 3/24, 1/8, ALL ONES, ZEROES, and POWER LOSS. Besides passing a combination of the 5 performance tests (determined by the type of T1 purchased) amd LOSS at the basic demarc (the Smart Jack) the same performance tests and loss must be passed at the Extended Demarc.


Forty six years and still fascinated with Telecommunications!
Joined: Oct 2010
Posts: 250
Member
Offline
Member
Joined: Oct 2010
Posts: 250
So you are sheilding, bonding, one side grounding as insurance. How you do it is your choice.


Forty six years and still fascinated with Telecommunications!
Joined: Oct 2010
Posts: 250
Member
Offline
Member
Joined: Oct 2010
Posts: 250
Use what ever wire you want sheilded, non sheilded, farm wire, open wire, barbed wire (in Wyoming barbed wire is called "twisted pair" as long as the tests parameters are met and maintained.


Forty six years and still fascinated with Telecommunications!
Joined: Aug 2009
Posts: 278
Member
Offline
Member
Joined: Aug 2009
Posts: 278
Quote
Originally posted by John Osvatic:
There is no NEC on T1 demarc extensions. What is regulated is what test parameters must be passed before telco can turn the T1 over to the customer. QRSS, 3/24, 1/8, ALL ONES, ZEROES, and POWER LOSS. Besides passing a combination of the 5 performance tests (determined by the type of T1 purchased) amd LOSS at the basic demarc (the Smart Jack) the same performance tests and loss must be passed at the Extended Demarc.
Okay, starting with nothing, what is the easiest and cheapest way to run these T1 tests at the extended demark?


Vaya con Dios amigos!
Butch
Page 2 of 3 1 2 3

Moderated by  Silversam 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,291
Posts638,815
Members49,767
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,425 Shoretel
189,196 CTX100 install
187,439 1a2 system
Newest Members
Robbks, A2A Networks, James D., Nadisale, andreww
49,767 Registered Users
Top Posters(30 Days)
Toner 26
teleco 6
dexman 5
jsaad 4
Who's Online Now
1 members (justbill), 163 guests, and 400 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5