Howdy all. I did 24 years with Nevada Bell now SBC. I now work for a small independent. My boss hates all things Bell so he and I are having a dispute on the subject of where the telephone protector or SNI or NID whatever you want to call it must be mounted on a residence . He insists that code requires that it be a minimum of four feet from the power panel . I have never heard of such a requirement. I not only need affirmation that one of us is nuts I also need where to find documentation. I have searched the N.E.C section 250 and can find nothing. THanks in advance for your help.
Don't fly the A model of anything
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Apr 2004
Posts: 4,991
Member
|
Member
Joined: Apr 2004
Posts: 4,991 |
I would think his impression comes from seeing both electric and phone coming off the pole and terminating in the same place on a residence.
If you take a poll while driving you will see them in every direction.
|
|
|
|
Joined: Jan 2005
Posts: 15,382 Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,382 Likes: 13 |
There's no formal (code) location requirement except that no more than 50 feet of unprotected cable may extend inside the building.
It is most convenient to obtain a good ground near the electric service. Since telco and electrical ground conductors must be bonded together (this IS a code requirment), common sense would dictate that they should be adjacent to each other. While a NID/protector can be installed anywhere on/in the building, a bonding wire would still have to be run to the electric service in order to be a "legal" installation.
Utility companies frequently use "joint" trenching on underground installations, resulting in the NID/protector being in the same area as the electric meter. Still, this isn't always the case. For aerial installations, the sky's the limit; I have seen NID's installed on window sills on the second floor!
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: Feb 2005
Posts: 12,347 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,347 Likes: 4 |
For aerial installations, the sky's the limit; I have seen NID's installed on window sills on the second floor!
Yeah so have I and they are absolutely useless as a protector. Where the hell do you ground it?
I have searched the N.E.C section 250 and can find nothing.
Try article 800. 250 as well as just about everything before 800 has nothing to do with communications unless you are specifically referred there. So for communications the NEC starts at 800.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Jan 2005
Posts: 15,382 Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,382 Likes: 13 |
I have only seen this done in Washington, DC installations. Verizon doesn't consider outside plant in the downtown area to be exposed (to lightning), so they don't use protectors there.
Even large feeder cables are just punched down on 66 blocks in office buildings; no protection at all.
NEC stipulates that any outdoor wiring that extends more than one city block be protected. Since Verizon is a utility, they are exempt from having to follow the NEC. They are also exempt from parking restrictions or so it seems!
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: Jun 2005
Posts: 512
Member
|
Member
Joined: Jun 2005
Posts: 512 |
There is a electrical code for outdoor service equipment. Which is any electrical meter and panel coming off that meter. NEC 110.26(A)& 110.26(F). The open zone around service equipment must have 6.6 feet head room, 3 foot in depth and 30 inches or width of equipment from side to side. So all you need to be safe is 30 inches.
|
|
|
|
Joined: Jun 2005
Posts: 512
Member
|
Member
Joined: Jun 2005
Posts: 512 |
That also appies to panels on the inside of a building or residence.
|
|
|
|
Joined: Sep 2005
Posts: 472
Member
|
Member
Joined: Sep 2005
Posts: 472 |
EV is right, the telephone and electric must be bonded in regards to ground. Standards require that any outside cable that extends beyond the shadow of protection (imagine a shadow being cast at a 45 degrees from top edge of buliding). When I was doing I&R we could put the interface anywhere as long the grounding requirements are met.
|
|
|
|
Joined: May 2002
Posts: 17,725 Likes: 19
Member
|
Member
Joined: May 2002
Posts: 17,725 Likes: 19 |
Originally posted by ev607797: I have only seen this done in Washington, DC installations. Verizon doesn't consider outside plant in the downtown area to be exposed (to lightning), so they don't use protectors there.
Even large feeder cables are just punched down on 66 blocks in office buildings; no protection at all.
NEC stipulates that any outdoor wiring that extends more than one city block be protected. Since Verizon is a utility, they are exempt from having to follow the NEC. They are also exempt from parking restrictions or so it seems! Man I'll get this right yet. Ed, this probably has to do with the part of the NEC on protection in areas of tall buildings. They claim if the buildings are x amount of feet above the cable you don't have to protect, because lighting will strike the building, not the cable. This is what I like about the NEC, you can read about anything you want into it, or find a section to contradict another. I'm sure Verizon and the others know how to do that very well $$$$.
Retired phone dude
|
|
|
|
Joined: Jun 2005
Posts: 512
Member
|
Member
Joined: Jun 2005
Posts: 512 |
Sageair-- Let me know what your boss says, when you tell him the minimum distance to mount anything by a service meter or panel is 30 inches, not 4 feet.
|
|
|
Forums84
Topics94,402
Posts639,370
Members49,808
|
Most Online5,661 May 23rd, 2018
|
|
1 members (nortelvoip),
145
guests, and
58
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
|