|
Joined: Jun 2001
Posts: 10,949
Moderator-Avaya
|
Moderator-Avaya
Joined: Jun 2001
Posts: 10,949 |
Hey fellows, I had to run some cat6 on the outside of a brick two story building.
No other choice, no where to take it on inside of wall.
There are two runs about 40 foot long. I ran 3/4 gray conduit and it is about 17 inches up on the biulding from the ground going horizonal.
Wire is not exsposed anywhere. Do you you all see any promlems with this? Or how I could improve it.
Thanks,
Avaya SMB Authorized Business Partner. ACIS/APSS ESI Certified Reseller/Installer www.regal-comm.com
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Sep 2005
Posts: 472
Member
|
Member
Joined: Sep 2005
Posts: 472 |
Some times you gotta do what you gotta do. Sounds like you did the best that could be done with a bad situation. It is high enough that you don't have to worry about weed eaters and other lawn weapons getting into the conduit. It should be fine! :thumb:
|
|
|
|
Joined: Jan 2005
Posts: 15,383 Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,383 Likes: 13 |
Mike:
You did more than your competition would have done. What you did was the only way to do it correctly; I think by using 3/4" conduit and fittings, you probably maintained minimum bend radius requirements, so it sounds like you are good to go. I say "good job"!
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: Jun 2001
Posts: 10,949
Moderator-Avaya
|
Moderator-Avaya
Joined: Jun 2001
Posts: 10,949 |
Is it best to use PVC or steel conduit on outside of building?
And if you say steel I guess it needs to grounded?
Avaya SMB Authorized Business Partner. ACIS/APSS ESI Certified Reseller/Installer www.regal-comm.com
|
|
|
|
Joined: Sep 2005
Posts: 472
Member
|
Member
Joined: Sep 2005
Posts: 472 |
PVC...Why? It's cheaper, it's easier to work with, and it doesn't corrode. Steel inside for plenum enviroments, firewall penetrations, etc... If you use steel outside it is always good to ground when possible but it is not always required. If it is within the buildings shadow of protection you shouldn't need the ground.
|
|
|
|
Joined: Jun 2001
Posts: 10,949
Moderator-Avaya
|
Moderator-Avaya
Joined: Jun 2001
Posts: 10,949 |
Well that was my next question and please correct me if I am wrong, but if you ground steel conduit that runs to the outside would'nt you create an oven for the wire inside in the case of an lighting storm?
Agian thanx,
Avaya SMB Authorized Business Partner. ACIS/APSS ESI Certified Reseller/Installer www.regal-comm.com
|
|
|
|
Joined: Sep 2005
Posts: 472
Member
|
Member
Joined: Sep 2005
Posts: 472 |
Yes, there is that possibility but if lightining strikes an outside steel conduit it will take the path of least resistance and if the conduit is not grounded it may very well follow your cable to it's terminated end. If that is your telephone system or your data switch it could be very nasty. Better your cable catch a little heat as the surge goes to ground then the inside equipment taking the hit and getting fried as well as potentially burning the building down.
|
|
|
|
Joined: Nov 2005
Posts: 32
Member
|
Member
Joined: Nov 2005
Posts: 32 |
I installed an exterior version of CAT5(thicker sheath,shielded and jell filled) about 3 years ago between 2 buildings that had no conduit between them and haven't had any problems. I can find the reel and get the manufacturer if your interested.They might have a CAT6 version by now.
Retired Telco 30 yrs.
|
|
|
|
Joined: Feb 2005
Posts: 12,347 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,347 Likes: 4 |
Is it best to use PVC or steel conduit on outside of building?
By steel I'm sure you mean EMT conduit (unless you are going to cut and thread). It certainly can be used outdoors but it is pretty much frowned upon because it corrodes so easily and there really isn't much steel there to begin with when it does. Better to use PVC.
As for grounding of EMT, there is no need or requirement as long as it's not likely to become energized. Most times when you are only sleeving LV cables this is going to be true.
I installed an exterior version of CAT5(thicker sheath,shielded and jell filled) about 3 years ago between 2 buildings that had no conduit between them and haven't had any problems.
It's designed for direct burial though I don't think I would want to do it that way unless it was only temporary.
However that is the stuff you would want to pull through buried conduit because the conduit will fill with water eventually.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Dec 2002
Posts: 341
Member
|
Member
Joined: Dec 2002
Posts: 341 |
I think in mdaniel's case I would have done the same thing (pvc). An electrician on one of our recent job sites was telling me that rigid steel is the only metal conduit NEC-approved for exterior use, but I haven't read the code myself, so I won't defend this. For underground LV we always use PVC, or maybe I should say the electricians always have "provided" pvc for us. I don't think that 40' of CMR in a pvc conduit should be any problem, since he's above ground and should have minimal condensation. If the conduit were underground, though, I'd be sure to use something rated for the purpose.
|
|
|
Forums84
Topics94,422
Posts639,464
Members49,818
|
Most Online5,661 May 23rd, 2018
|
|
0 members (),
199
guests, and
622
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
|