When I refer to a smart jack, I am thinking of the "electrical interface" type of smart jack. Are they known by something else? The telco can send a loop up/down command to the termination point and test the line out.

Ok...why would the telco terminate on a 66 block over one of the devices I describe above?

The answers will lead me onto more questions but I'll use this as a starting point.

Regards,

Rick

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Sep 2004
Posts: 1,436
Member
Member
Joined: Sep 2004
Posts: 1,436
The smart jack is typically a box on the wall with some lights and at least one circuit board visible behind a clear plastic cover, has at least one RJ45 jack, and a cable going to either the RJ21x block or other demarc. The smart jack converts the incoming 2 pair line to an RJ45 T1 or PRI line, you need a CSU/DSU between it and your equipment to handle the protocol translation. The smart jack and the cable going to it are the phone company's property and their responsibility to fix.


Joe
---
No trees were harmed as a result of this posting; however, many electrons were severely inconvenienced.
Joined: Oct 2004
Posts: 684
Member
Member
Offline
Joined: Oct 2004
Posts: 684
In a word lazy.

Many times here they will leave circuits on the outside of the building.

Joined: Nov 2001
Posts: 1,640
Moderator-NEC
*****
Moderator-NEC
*****
Joined: Nov 2001
Posts: 1,640
Often the SMARTJACKS for an office building are in the Main phone room/closet where all of the phone lines come in, and there is a "shelf" with many circuits (smartjacks)in it.
The individual smartjacks are extended to the particular office suite via the 25 pair feed cables to the 66 block in the office. Generally they are then hooked up to a special RJ48X jacks with shorting bars in them.

~Don~

Joined: May 2002
Posts: 17,725
Likes: 18
Member
****
Member
****
Joined: May 2002
Posts: 17,725
Likes: 18
A smart jack is nothing more than a jack with shorting bars that put a loop on the circuit when the modular cord is unplugged. The unit you are taking about, where telco sends out a 2713hz freq. to loop up to test the circuit is ahead of the smart jack. Some loop back devices do have a "smart jack" internally wired to keep the circuit "alive" if it's unplugged.

Sorry to complete your question if they bypass the loop back deivice the circuit couldn't be balances as all the gain and slope settings are in that loop back unit. Old ones were simply called 829's
Bill

[This message has been edited by justbill (edited January 31, 2005).]


Retired phone dude
Joined: Jan 2005
Posts: 2
Member
Member
Offline
Joined: Jan 2005
Posts: 2
Thanks for the answers. So in a perfect world, the telco would terminate on an 829 at the telco entry point for the facilty then extend the circuit to the modular jack w/shorting bars. Right? I've always refered to the 829's as Smart Jacks...incorrectly I guess.

Next Question:

When the telco terminates a T-1 in a facility, it has to have a certain amount of signal strenght, right? And is this signal strength measured in gain? And if the signal strength is a bit on the low side, can they increase the gain or adjust the LBO for that T-1? If so, where would they do the adjustment...at the 829?

Again...thanks in advance for your help!!

Joined: Jul 2003
Posts: 766
SST Offline
Member
Member
Offline
Joined: Jul 2003
Posts: 766
Smart jack is another abused term, It kind of' depends on who you talk with and you will get some different answers. The NIU (Network Interface Unit) is most often called the smart jack. The NIU is usually the Telco’s d-marc unless extended by them, usually on a 48x jack (shorting pins) or 48c jack (no shorting pins). The 48x is sometimes called a smart jack because of the shorting pins. The NIU is remote loopable from the C.O. There are many varieties of NIU's but all pretty much do the same thing. They provide demarcation; a testing point, protection, line status and some log a trouble history. T1 NIU's are looped with digital codes. The 2713Hz is for looping dedicated analog ckts. like 9.6 ckts. Etc....

Joined: Oct 2004
Posts: 684
Member
Member
Offline
Joined: Oct 2004
Posts: 684
WOW you guys got it made. If I get label I think its a good day. Jacks and everything huh?

Joined: May 2002
Posts: 17,725
Likes: 18
Member
****
Member
****
Joined: May 2002
Posts: 17,725
Likes: 18
SST is correct, was having a senior moment. The Network interface unit it where telco hands off a T-1, unless the sub pays for an extended DEMARC. Sorry about taking you down the wrong path. As SST stated the 829 type loop back units are for private line data type services. Your other question on levels is yes there are level requirements, but depends on how you get the T-1 as to what they are...and again this is a senior memory taking to ya. Fiber is 0 db and if I remember right copper is -8 db.


Retired phone dude
Joined: Sep 2005
Posts: 22
Member
Member
Offline
Joined: Sep 2005
Posts: 22
T1 Smart Jacks, AKA: T1 NIU's, depending on the LEC, perform more than just loopback continuity functions. The lates generation of T1-NIU's also contain Performance Monitoring, or PM, data. PM data is monitored in both direction of the T1 signal path. Typical PM data collected would be BPV, Loss Of Signal, excessive zero's (Line events), and Path Errors, such as CRC-6 for ESF, frame bit errors for SF frammed circuits. Timing slips are not typically tracked by NIU's. One other usefull function by most current Ti-NIU's is that it hasthe ability to notify the network (Telco CO) that the CPE has either been disconnected, of has failed at the input. When a T1 circuit losses framing into the NIU, and where the signal has degraded to the point where upstream MUX equipment invokes an unframed all ones (AIS), the T1-NIU will send a modified AIS known as AIS-CI. AIS-CI, and RAI-CI, CPE fault yellow alarm, have been in the ANSI standards since the late 90's. Typical CPE eight pin jack interfaces are configured as RJ48C. The 48X interface has been phased out by "most" Telco's since it would defeat the AIS-CI feature should the CPE disconnect from the network interface. One additional note. HDSL remote units have incorporated the very same, if not similar operational functions of T1-NIU's, to include in-band loop up/down support for FT1 circuits (Verizon Territory) using the DDS NEI/RPTR loop codes.

Joined: May 2002
Posts: 17,725
Likes: 18
Member
****
Member
****
Joined: May 2002
Posts: 17,725
Likes: 18
Hey Field ops, welcome. I remember those units and we could also access them remotely, if I remember right (see age related issues in this post) on remote testing you had to think backwards or what you saw in the PM data would mess with your head. Keep in mind these were very new at the time.


Retired phone dude
Joined: Feb 2005
Posts: 102
Member
Member
Offline
Joined: Feb 2005
Posts: 102
"CPE fault Yellow alarm" may be an ANSI standard from the late 90's but the bell system has had it from before 1970. The old D1B carrer system only had two signal alamrs red and amber(yellow). Red was when the system could not see a signal it could sync to. amber was a signal sent by a system with a red alarm to tell the other end that it could not see its signal.

Joined: May 2002
Posts: 17,725
Likes: 18
Member
****
Member
****
Joined: May 2002
Posts: 17,725
Likes: 18
I think a lot of the ANSI standards came from the old Bell system standards.


Retired phone dude
Joined: Feb 2005
Posts: 40
Member
Member
Offline
Joined: Feb 2005
Posts: 40
I have a T1 on an InterTel Axxess system that keeps dropping into red alarm, When I called in the tech said to look at the LED's on the smartjack. I show Power lit green and ESF lit green but flucuating.

Question is What is ESF? Should it be flucuating? and is this an indication of a problem with our provider.


Dan L Armstrong
WinWholesale
Joined: Jan 2005
Posts: 15,382
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,382
Likes: 13
Usually, if the ESF light is lit, then the T1 is configured for Extended Super Frame (ISDN-PRI). If it's not lit, it is configured differently or there is a problem with the circuit. I just checked ours here and it's lit steady. A few weeks ago, our circuit went out a few times and each time, the ESF light was flickering. My guess would be that you definitely have a problem with the circuit from your service provider.


Ed Vaughn, MBSWWYPBX
Joined: Jul 2005
Posts: 860
Member
*****
Member
*****
Joined: Jul 2005
Posts: 860
Wow… You dug up an oldie but a goodie with this post! wink

ESF= Extended Super Frame
No, it should not be bouncing. You’re getting framing errors for some reason. That would be a Telco issue they need to resolve.


-----------------------
Bryan
LEC Provisioning Engineer
Cars -n- Guitars Racin' (retired racer Oct.'07)
Joined: Feb 2005
Posts: 40
Member
Member
Offline
Joined: Feb 2005
Posts: 40
Excellent. Thanks for the help folks. I am by no means a newbie to this phone stuff, but I'm never sure whether to call our InterTel or Sprint. Finding these forums is the best thing I ever did!

Thanks again for your help.


Dan L Armstrong
WinWholesale
Joined: Aug 2006
Posts: 185
Member
Member
Offline
Joined: Aug 2006
Posts: 185
Maybe getting a CSU that is "Smart" something like the Kentrox T-Smart would help as a test tool. It will let you see which way the errors are coming from you or the network.

Joined: Sep 2008
Posts: 1
Member
Member
Offline
Joined: Sep 2008
Posts: 1
Does a Smart Jack need to be plugged into local AC power or is power provided by telco?

Joined: Jan 2005
Posts: 15,382
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,382
Likes: 13
If you are referring to a T1 termination card mounting, A.K.A: NIU, then the answer is probably no. Most stand-alone circuits are line powered these days.

It is generally better if you start your own new thread instead of tagging onto an old one. That way you will receive a response more promptly. This original thread dates back to 2005!

welcome


Ed Vaughn, MBSWWYPBX
Joined: May 2007
Posts: 5,058
Likes: 5
Moderator-1A2, Cabling
*****
Moderator-1A2, Cabling
*****
Joined: May 2007
Posts: 5,058
Likes: 5
Ed -

When I worked for the Independent Carriers (AT&T, Nextlink, Winstar, ART, Teligent, Telergy etc.) ALL the smartjacks were locally powered. The only ones I ever saw that were line powered were the ones from Bell Atlantic.

Sam


"Where are we going and why are we in this hand basket?"
Joined: Jul 2005
Posts: 860
Member
*****
Member
*****
Joined: Jul 2005
Posts: 860
Holly old posts Batman… eek

Like Ed said most NIU’s or NID’s (network interface devices) aka “smart jacks” are line powered.


-----------------------
Bryan
LEC Provisioning Engineer
Cars -n- Guitars Racin' (retired racer Oct.'07)
Joined: Nov 2008
Posts: 65
Member
Member
Offline
Joined: Nov 2008
Posts: 65
Depends on the type of smartjack and the carrier...some are line powered, some are locally powered. Can't really say it'll be one way or the other. I've seen plenty of both.


--Matt
Page 3 of 3 1 2 3

Moderated by  Silversam 

Link Copied to Clipboard
Newest Topics
Vertical Summit transfer issue
by ljclives - 09/18/24 09:48 AM
Retired and ?
by John807 - 09/17/24 01:03 PM
Need hard reset of TD308
by Alan_G - 09/16/24 12:03 PM
DB Programming Software for 8.235
by LukeE. - 09/10/24 07:36 PM
Forum Statistics
Forums84
Topics94,395
Posts639,309
Members49,804
Most Online5,661
May 23rd, 2018
Newest Members
LukeE., BurleyTech, Kobusvant, irjeffb, ALEXKINGTHESUN
49,804 Registered Users
Top Posters(30 Days)
Toner 15
dexman 9
Seth W 8
teleco 6
pvj 5
Who's Online Now
1 members (Yoda), 326 guests, and 387 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998 - 2024
Powered by UBB.threads™ PHP Forum Software 8.0.0