Joined: Dec 2013
Posts: 2
Member
|
OP
Member
Joined: Dec 2013
Posts: 2 |
I have a customer who's requirement involves having a new 70v paging system (Valcom) with multiple zone be overidden at will by a Whelen emergency 70v system. The Whelen system has to be able to take over the speakers and shut out the new system in the event of a emergency broadcast. My main problem is figuring out if it is possible set up two 70v systems that can switch back and forth on some type of relay. I Cant find any equipment that exists that will perform this task. Anybody have any suggestions?
BBTech
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Feb 2005
Posts: 12,335 Likes: 3
Member
|
Member
Joined: Feb 2005
Posts: 12,335 Likes: 3 |
Easy enough to roll your own with suitable relays. That said, the Whelan sounds like a life-safety system and there are strict rules for installation and operation that probably aren't met by the paging speakers.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Feb 2005
Posts: 12,335 Likes: 3
Member
|
Member
Joined: Feb 2005
Posts: 12,335 Likes: 3 |
I second the recommendation for dbx however I think that it's going to require a total re-design of the system. I believe the Whelen system is self contained with it's own 70v output.
Does the Whelen provide PA capability or just warning tones?
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Jan 2013
Posts: 519 Likes: 1
Member
|
Member
Joined: Jan 2013
Posts: 519 Likes: 1 |
I have a customer who's requirement involves having a new 70v paging system (Valcom) with multiple zone be overidden at will by a Whelen emergency 70v system. The Whelen system has to be able to take over the speakers and shut out the new system in the event of a emergency broadcast. My main problem is figuring out if it is possible set up two 70v systems that can switch back and forth on some type of relay. I Cant find any equipment that exists that will perform this task. Anybody have any suggestions?
BBTech One problem your going to have is unless the equipment is listed by your State Fire Marshall, you can't connect it to the fire alarm system. I don't know the Whelen system, but I do know the Silent Knight systems and they have devices that will do what you want and are listed. You need to ask this question to someone qualified in the Whelen system.
Patrick T. Caezza Santa Paula, CA 93060 C-7 - Low Voltage System Contractor - Lic# 992448
|
|
|
|
Joined: Feb 2005
Posts: 12,335 Likes: 3
Member
|
Member
Joined: Feb 2005
Posts: 12,335 Likes: 3 |
Whelen makes emergency and mass notification systems so I have no doubt that it can be interconnected with a fire system. The question is is it allowable to use the Valcom speakers with a life-safety or mass notification system. I seriously doubt it. And yes, you do need to talk with someone qualified on Whelen systems.
-Hal
|
|
|
|
Joined: Dec 2013
Posts: 2
Member
|
OP
Member
Joined: Dec 2013
Posts: 2 |
Thanks for the info guys!!! The Whelen provides PA also. Its like they want to merge they systems in case of emergency. Odd situation. I'm looking at the dbx equipment now.
|
|
|